What size branch-circuit conductors are required for the welder indicated in Ta...

✅ The verified answer to this question is available below. Our community-reviewed solutions help you understand the material better.

What size branch-circuit conductors are required for

the welder indicated in Table 13-2 in your book? 

There is no marked

termination temperature found on the equipment.

 Use 230 volts , 90 A

and 100% duty cycle:

 Conductor  use will be RW90XLPE copper 

0%
100%
0%
0%
0%